Treane heat pump freeze-up
I'm a recently hired employee of a medium sized school district and have myriads of different types of HVAC equipment. I'm fairly new to Trane heat pumps, with their electronic defrost system, and am a little stumped. We have 2 schools with this brand of heat pump where one unit will not initiate defrost and the next one will (about 15 0f 30). Upon manual defrost, pressures on both high and low sides look comparable and in test mode will defrost. I've replaced the "silver bullet" thermistor sensor at the evaporator base, swapped control boards and cleaned seemingly pristine outdoor coils as a last ditch effort. What am I missing?