Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Heating & Air Conditioning (https://www.askmehelpdesk.com/forumdisplay.php?f=150)
-   -   Troubleshooting a Intertherm Furnace Model mmhb-090abhr-06? (https://www.askmehelpdesk.com/showthread.php?t=788189)

  • Mar 30, 2014, 07:37 PM
    jermwelsh
    Troubleshooting a Intertherm Furnace Model mmhb-090abhr-06?
    Came home from a long weekend and found the house cold. One flash, I shut down the furnace and restarted. Everything worked except the fan would not turn on also the furnace did not shut down and give me the same code. So I just turned the furnace off. The fan will work when I place the switch on fan. I am guessing it is the fan switch.
  • Apr 1, 2014, 07:31 PM
    Grady White
    If the fan is controlled off a circuit board, the relay for the fan in the heating speed is probably shot. You can test by measuring voltage from the fan 'heat' terminal to neutral. After a few seconds of the burner firing (no longer that probably 30 seconds) you should get 120 volts AC from that terminal. If you do, the problem is not the board.