  • Mar 4, 2014, 06:30 PM
    greg_bird2001
    Have a 100 amp service
    I have a 100 amp service ,I want to put a 20 kw furnace in ,will 2 6 gauge 220 wires be right
  • Mar 4, 2014, 07:22 PM
    ma0641
    What else is on the service?
  • Mar 4, 2014, 07:43 PM
    Grady White
    20kw at 240 volts is going to draw 83.33 amps. Number 6 wire is no where near heavy enough.