    Hiel furance m #nugk100dh08
    Theromsat calls for heat inducer fan come on vacu switch closess pilot lights burners come on and stay on for about 2 to 3 minute, burners go off inducer fan stopes stay off for about 1 to 2 minute then cyle starter any and keeps on doing this. Is the problem the ignition modules witch is part #hq1oo5962ex
  • Feb 18, 2014, 03:47 AM
    parttime
    Hi s and welcome, It don't sound like you have an ignition problem, you say the burner is coming on. I'd lean more to a flame sensor. These can be cleaned using steel wool. Good luck
  • Feb 20, 2014, 05:10 PM
    edward3
    Hi there, May want to also check limit controls, That may be the safety control that is tripping out. Hopefully this will help you out .