  • Feb 2, 2014, 03:54 PM
    jimmarquardt
    Free electrical questions
    I have a 220 welder plugged into a 30 amp breaker and a 50 amp rated plug. I just bought a 220 compressor and was wondering if I could make or have made a short cord with an adapter to plug into the 50 amp plug?
  • Feb 3, 2014, 04:39 AM
    hfcarson
    You can do anything you choose...
    What is your real question?
  • Feb 3, 2014, 11:32 AM
    donf
    You might want to stop and think just a tad, here. Just for the record, the nominal voltage is now 240, not 220 but that is not an issue. Motor branch circuits are a different breed of branch circuit.

    You have given us only one piece of valid information. A 30 amp circuit connected to a 50 amp receptacle for a cord and plug welder. Perfectly acceptable.

    This proposed compressor, does it require a 30 amp branch circuit using 240 volts?

    Motor circuits are not calculated the same way a general branch circuit is calculated.

    The breaker may be required to be quite a bit higher in amperage to allow for the "Start Inrush Amperage" needed by the motor. Also, a motor conductor is required to be sized at 125%.