-   -   Single flash on circuit board (https://www.askmehelpdesk.com/showthread.php?t=782408)

  • Jan 24, 2014, 04:28 PM
    swat987
    Single flash on circuit board
    Blower fan comes on immediately. Furnace will not fire. Circuit board single flash... limit circuit open or external load on "W"
  • Feb 1, 2014, 03:05 PM
    Kukui23
    Limit Circuits are usually high limit thermostats. If it is resettable, push the button, if not resettable, replace the high limit stat. You will need a wiring diagram and possibly a parts blow up to locate the stat as well as a multimeter to see if the high limit stat is open. The W wire is the one that enables the furnace from the stat. It should be just a relay with no load on it... basically a contact switch. Perhaps that wire doesn't have enough voltage running to the furnace so it detects a "load" on it.

    I'd start with the hi limit stats though.