    Trane xb80 blower motor reset
    I have a XB80 gas heating unit.
    I noticed the blower motor has stopped working. Is there a way to reset it after changing all the filters and a complete vacuuming.
  • Dec 22, 2013, 08:07 PM
    ma0641
    There may by a high temp shutoff but if it ran super hot it may have burned the motor out. Have you tested the capacitor? Does the motor try to start?
  • Dec 22, 2013, 08:58 PM
    Grady White
    After the furnace has been on for 30 seconds or so, measure voltage between the heaing speed fan terminal & neutral. You should get +/- 120volts AC. If you do not, the board is likely bad.