The minimum size copper equipment grounding conductor required on a motor branch circuit with a 30 amp circuit breaker and 12 awg copper counductors is
![]() |
The minimum size copper equipment grounding conductor required on a motor branch circuit with a 30 amp circuit breaker and 12 awg copper counductors is
You can read the NEC online and find the answer. Hope this is a 240 circuit, otherwise itbis way over permitted amperage.
The voltage has nothing to do with the amperage/wire size relationship.Quote:
Hope this is a 240 circuit, otherwise itbis way over permitted amperage.
If's a motor branch circuit so #12 on a 30A is perfectly feasible.
Do your own homework. It's all in the NEC and your study guides.Quote:
The minimum size copper equipment grounding conductor required on a motor branch circuit with a 30 amp circuit breaker and 12 awg copper counductors is
Why not tell us what you think it is and how you get it and we'll go over it?