Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Heating & Air Conditioning (https://www.askmehelpdesk.com/forumdisplay.php?f=150)
-   -   Igniter on the furnace is not glowing, motor starts and then shuts down. (https://www.askmehelpdesk.com/showthread.php?t=777136)

  • Nov 30, 2013, 01:55 PM
    Sharhi
    Igniter on the furnace is not glowing, motor starts and then shuts down.
    Goodman high efficiency furnace.
    Furnace has been shutting off periodically, for a few hours at a time and then starting up on its own.

    Sometimes when I would change the temp. it would start up again at the same time. But now...
    The igniter does not glow when I restart it (after turning off the power) and it just shuts off, tries to start a second time and then shuts off again after a valiant effort.

    Seems the igniter is not working. Cannot see any glow or burner flame during this process or at all. (Have pulled the back off to see better).
    Is this a cleaning problem? Can anyone tell me where to start?
  • Nov 30, 2013, 05:56 PM
    ma0641
    You will need to check a couple of things. First, look for the fuse on the control board and check it. If it is OK you will need to check for voltage at the control panel. Is the induced fan running?
  • Nov 30, 2013, 07:53 PM
    Grady White
    Do you have a voltmeter & know how to use it?