  • Oct 29, 2013, 06:33 AM
    makingmoney123
    Using single phase breaker in three phase panel
    I have two spaces left in a three phase 240 volt panel, I want to install a single phase 240 volt breaker for a compressor. Is this OK if one of legs is the "high leg"?
  • Oct 29, 2013, 09:55 AM
    hfcarson
    Yes, as long as you are careful of any 120V loads or controls...
    There is usually a small control transformer. If it is a 240V transformer you
    Are OK, if it's a 120V then be careful which leg it connects to...