Hi, I have a boiler and tried to get rid of the old thermostat but made the mistake of not writing down where each wire should go. I tested voltage and continuity:
Basement, 4 wires
From Trasnsformer: Yellow and Brown and I tested 26V
From Extra box (not sure what this does) Red and Black wires with Zero Voltage
Main Floor, 4 Wires
Yellow, Blue, Red, Black and there's 26V between the Blue and Yellow wires.
This is the continuity I tested
Yellow basement goes to Yellow on the wall, Red goes to Red, black goes to black. BUT the Brown wire from the transformer has no continuity with the Blue on the wall.
Appreciate any thoughts on how to wire my thermostat