  • Oct 9, 2013, 01:35 PM
    tmoua9580
    Bryant plus 80 furnace won't ignite burner
    I own a Bryant Plus 80 gas furnace. The fan will run if I set the thermostat to "Fan On" instead of "Fan Auto". But the burners will not ignite. It was working fine until I got my gas shut off. When I got my gas returned on the furnace won't ignite anymore.
  • Oct 9, 2013, 02:24 PM
    WallyHelps
    1 Attachment(s)
    There should be a valve near the furnace. Make sure it is on. Have someone turn the thermostat to a high temperature while you are right in front of the furnace and see if you can hear/smell gas while it tries to start.

    Good luck,
    WallyH
  • Oct 9, 2013, 04:31 PM
    tmoua9580
    Quote:

    Originally Posted by WallyHelps View Post
    There should be a valve near the furnace. Make sure it is on. Have someone turn the thermostat to a high temperature while you are right in front of the furnace and see if you can hear/smell gas while it tries to start.

    Good luck,
    WallyH

    I try that and there is no gas.. I have gas to the boiler n my gas stove
  • Oct 10, 2013, 06:31 AM
    tmoua9580
    I try that and there is no gas.. I have gas to the boiler n my gas stove..
    I also want to know if the polite could be dead or needs to reset.. In this case
  • Oct 10, 2013, 07:17 PM
    Grady White
    If the furnace has a pilot which stays lit all the time, the pilot will need to be re-lit before you are going to get any heat.
  • Oct 11, 2013, 06:43 AM
    tmoua9580
    It is a automatic polite.. That means I don't need to light the polite.. When I turn on heat n auto nothing kicks on.. But when I turn on heat n fan.. I hear is just the fan blowing, no flames
  • Oct 11, 2013, 06:36 PM
    Grady White
    Is there a small exhaust blower & if so does it run? Does the furnace light via a spark ignited pilot or is there normally a glow plug which lights the burners?
  • Oct 12, 2013, 07:33 AM
    tmoua9580
    Where can I find the exhaust blower. In the past when ever I turn on heat plus auto I hear a click sound then everything's works but now I don't hear anything
  • Oct 12, 2013, 06:29 PM
    Grady White
    The exhaust blower, more properly called venter or draft inducer, connects to the exhaust pipe.
  • Oct 12, 2013, 06:44 PM
    tmoua9580
    Ok.. The exhaust blower doesn't make a sound..
  • Oct 13, 2013, 06:57 PM
    Grady White
    Make sure the door to the blower compartment is properly installed. If it is, check on the control board for a small automotive type fuse (usually either 3 or 5 amp).
  • Oct 14, 2013, 01:23 PM
    tmoua9580
    Everything is in place and the fuse is properly installed. The fuse is not blown. The LED light is just at solid. No blinking light from the LED
  • Oct 14, 2013, 03:30 PM
    Grady White
    Install a jumper wire between terminals R & W. You will probably have to hold the blower door switch in but this will by pass the thermostat & it's wiring. If the furnace now runs, you have a problem either with the stat or the wiring between the stat & furnace.
  • Oct 14, 2013, 04:20 PM
    tmoua9580
    Where can I find the terminals R & W.
    Wire..
  • Oct 15, 2013, 08:08 PM
    Grady White
    Follow the thermostat wires where they go into the furnace.