  • Oct 8, 2013, 11:34 AM
    mike918
    Pilot Light Will Not Stay Lite on my natural gas furance after I installed a new pilo
    My pilot lite will not stay lite after I replaced the pilot/thermocoupler with a new one because the old one did the same thing
  • Oct 8, 2013, 07:46 PM
    Grady White
    You need to confirm you are getting the correct voltage from the thermocouple. That voltage is most commonly around 30 millivolts DC. If you are getting the correct voltage & the thermocouple was snugly installed into the gas valve, you probably have a bad gas valve.
  • Oct 9, 2013, 03:20 PM
    mike918
    Quote:

    Originally Posted by Grady White View Post
    You need to confirm you are getting the correct voltage from the thermocouple. That voltage is most commonly around 30 millivolts DC. If you are getting the correct voltage & the thermocouple was snugly installed into the gas valve, you probably have a bad gas valve.

    Thank you I will check and let you know what happens