Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Heating & Air Conditioning (https://www.askmehelpdesk.com/forumdisplay.php?f=150)
-   -   Changing thermostat (https://www.askmehelpdesk.com/showthread.php?t=767016)

  • Sep 13, 2013, 10:43 AM
    B1gd4ddy813
    Changing thermostat
    I have an old trane baystat 239 and want to change it out with a Honeywell th5220. Can't find out color differences
    Trane.
    Black = x2
    Orange = o
    Green = g
    Yellow = y
    Brown = T
    Red = R
    White = w
    Blue = B

    Any help would b grateful
    Thanks
  • Sep 13, 2013, 01:55 PM
    dewey066
    Basically this is what Honeywell came up with for terminal designations:

    W, W1, W2 - Heat Relay (1 and 2 means single or dual-stage heat)
    Y, Y1, Y2 - Cooling Relay(s)
    G - Fan Relay
    R - "High-Side" of 24V Transformer
    C - "Common-Side" of 24V Transformer

    O and B Terminals are either used for a reversing valve if it is a Heat Pump, or if there is a zoning/damper panel it is used to put it in Heating or Cooling Mode (B - Heating Mode, O - Cooling Mode).
    ***If you have an older zoning panel with both the O and B terminals then you will need a thermostat with both of those terminals - A Honeywell 3000 or 4000 has both***

    NOTE: B Trane sometimes used it as their Common Terminal "C"
    T - could be a heat anticipator/outdoor reset.
    X2 - Could be second stage of electric heat on a Trane unit. Also could be air flow sensor, or LED's

    I hope this helps. If you provide more info I can be more specific: Is this a heat pump? Is there zone dampers? Is there an outdoor sensor? Is there a sensor in the supply duct? Are there electric heat elements in the air handler?