  • Sep 13, 2013, 08:57 AM
    will525
    Nordyne furnace diagnostics 2 blinks followed by a pop noise then humming noise
    I have reset the power to the furnace. Every time it flashes 2 times which says it is the pressure switch is open with inducer on. It makes a popping noise as soon as it has power to it. Then that noise goes away and I have a steady humming noise after that. Nothing at all happens. This is the first time I have tried to use it this year. It worked fine last year. Please help if you can.
  • Sep 13, 2013, 06:02 PM
    Grady White
    This is most likely the result of a stuck pressure switch but it could also indicate a restriction in the intake or exhaust system. Does the inducer motor come on?
  • Sep 14, 2013, 09:32 AM
    will525
    Quote:

    Originally Posted by Grady White View Post
    This is most likely the result of a stuck pressure switch but it could also indicate a restriction in the intake or exhaust system. Does the inducer motor come on?

    No sir it does not come on and thank you for the reply.
  • Sep 14, 2013, 04:32 PM
    Grady White
    Check to see if you are getting 120 volts to the inducer motor. If so, shut off the power & if possible try to turn the motor manually. On some inducers you can turn the cooling fins with a small screwdriver. If you can turn it, try starting the furnace again. Sometimes the motors will stick over the summer.