  • Jul 29, 2013, 09:13 PM
    nathanscott44
    Air handler problem
    Have a american standard twe air handler. The motor seems to be turning slow. The dip switches are set for high speed. Having problem with evap freezing. The charge seems good. Getting a fault code on cfm led of 7 blinks and roughly 8-10 secs of solid green. Any ideas? Thanks
  • Jul 30, 2013, 07:32 PM
    Grady White
    It sounds like you have an ECM motor on the fan & either the control side of the motor or the control board in the air handler has gone bad. My guess is it is the control side of the motor. A tech could tell for sure.