Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Heating & Air Conditioning (https://www.askmehelpdesk.com/forumdisplay.php?f=150)
-   -   Pipe freezing over (https://www.askmehelpdesk.com/showthread.php?t=758988)

  • Jul 19, 2013, 01:50 PM
    theoali
    Pipe freezing over
    I've narrowed it down to when my system freezes over but don't know why it is doing it. On my thermostat, if I turn the system "off" and put the fan to "auto" rather than "on", within an hour, the pipe coming into the house to my unit freezes up. Also, when it's in this state, my unit outside never stops working. If I have the system "off" and the fan "on", it does not freeze over

    Hopefully I can get some answers

    Cory
  • Jul 19, 2013, 03:36 PM
    Joshdta
    If fan is running then either air filter is cloged up or unit is low on freon. With system off ac is not running so it can't freeze
  • Jul 19, 2013, 06:40 PM
    theoali
    Quote:

    Originally Posted by Joshdta View Post
    if fan is running then either air filter is cloged up or unit is low on freon. With system off ac is not running so it can't freeze

    A friend of mine said it could be a defective thermostat considering the outside unit runs at all times
  • Jul 19, 2013, 06:47 PM
    Joshdta
    Doe the outdoor unit shut off with the t-stat set to off??
  • Jul 20, 2013, 06:54 AM
    theoali
    Quote:

    Originally Posted by Joshdta View Post
    doe the outdoor unit shut off with the t-stat set to off???

    No, the "T" stat is set to off and the unit outside is still going, the only time I've seen it stop is if I flip the breaker
  • Jul 20, 2013, 04:55 PM
    Grady White
    Will the outdoor unit shut off if you turn off the power to the furnace at the breaker? If not, it sounds to me like a contactor welded shut.
  • Jul 20, 2013, 06:48 PM
    Joshdta
    I agree sounds like you need a new contactor on the outdoor unit
  • Jul 21, 2013, 06:32 AM
    theoali
    Quote:

    Originally Posted by Joshdta View Post
    i agree sounds like you need a new contactor on the outdoor unit

    The unit outside shuts off if I turn off the breaker
  • Jul 21, 2013, 07:21 AM
    Joshdta
    https://www.google.com/search?q=ac+c...ml%3B360%3B360


    Make sure you turn breaker off to indoor and outdoor unit before replacing
  • Jul 22, 2013, 06:22 PM
    Grady White
    Quote:

    Originally Posted by theoali View Post
    the unit outside shuts off if i turn off the breaker

    Does the outdoor unit shut off only when you turn off it's breaker OR will it shut off if you turn off the FURNACE breaker? If it shuts off when the furnace breaker is turned off, the contactor is NOT the problem.
  • Jul 23, 2013, 07:18 AM
    theoali
    The heat pump unit outside ONLY shutsdown when I turn off it's own breaker. It does not shut down when I turn off the Furnace breaker
  • Jul 23, 2013, 04:19 PM
    Joshdta
    Contactor is bad
  • Jul 23, 2013, 06:37 PM
    Grady White
    Quote:

    Originally Posted by Joshdta View Post
    contactor is bad

    I concur.