    Black30
    New outlet / service panel with no ground
    How to ground a 240v outlet in a service panel with ground bar?
  • Jul 10, 2013, 06:28 AM
    hfcarson
    This is a basic installation... can you be more specific with your question?
  • Jul 11, 2013, 10:45 AM
    Black30
    The service panel has there hot lines,
    One neutral bus and no grounding bar. Where does the grounding wire from the new 240v outlet go? Can it be connected to the neutral bus?
  • Jul 11, 2013, 10:55 AM
    hfcarson
    Is this the main panel in the building? If so, then both Neutral and Equipment Ground conductors terminate on the Neutral bar.
    Verify that the Neutral bar is "bonded" to the panel enclosure.
  • Jul 11, 2013, 01:46 PM
    stanfortyman
    Where is this? Is it a commercial building?
  • Jul 12, 2013, 08:21 AM
    Black30
    Commercial building in the Bronx,NY.
  • Jul 12, 2013, 08:36 AM
    hfcarson
    Does the panel in question contain the "Service Disconnect" for the building?
    Or is this panel the second of third in the building...
  • Jul 12, 2013, 11:25 AM
    stanfortyman
    Quote:

    Commercial building in the Bronx,NY.
    All electrical work in NYC requires a licensed electrician.
  • Jul 13, 2013, 10:16 AM
    hfcarson
    There are dozens of ways to do this wrong... your silence is one of them