  • Jun 26, 2013, 11:16 AM
    nasran
    My well has a double 50 amp (240 volt) breaker.. what is max amps could pull
    I am looking to size a generator for my house (emergency only) I want to size it as a minimum to be able to run my well pump which has a double 50 amp breaker (240 v). What is the max amps the pump can pull based upon that breaker... is it 50 amps or 100 amps.
  • Jun 26, 2013, 11:27 AM
    smoothy
    You don't need a generator for your freezer or refrigerator.. or anything else in your house... just the well?
  • Jun 26, 2013, 11:31 AM
    hfcarson
    ... at 240V the breaker will trip at 50A...

    Be advised you cannot now say that you need a 50A, 240V generator...
    The appropriate genset size will likely be at least 50A x 125%...
    The genset sales people will size and make recommendation for you...
    If you know a good electrician I would rather trust him than a salesmen...
  • Jun 26, 2013, 11:50 AM
    stanfortyman
    A well on a 50A breaker? Something is not right.
  • Jun 26, 2013, 12:13 PM
    smoothy
    Quote:

    Originally Posted by stanfortyman View Post
    A well on a 50A breaker? Something is not right.

    Maybe it supplies the water tower for a small town.
  • Jun 26, 2013, 05:17 PM
    Kyle_in_rure
    Quote:

    Originally Posted by stanfortyman View Post
    A well on a 50A breaker? Something is not right.

    My thoughts exactly.

    Nasran, do you know the horsepower of your pump? You can't really just go off the breaker amperage.

  • All times are GMT -7. The time now is 01:43 AM.