Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Heating & Air Conditioning (https://www.askmehelpdesk.com/forumdisplay.php?f=150)
-   -   How do you wire a hvac fan motor that doesn't require a capacitor (https://www.askmehelpdesk.com/showthread.php?t=754107)

  • Jun 17, 2013, 09:27 AM
    maindoug321
    How do you wire a hvac fan motor that doesn't require a capacitor
    I replaced the fan motor on the condensing unit. The motor says it does not require a capacitor. When I install the fan wire into the existing capacitor the fan runs continuously. Can the capacitor be eliminated?
  • Jun 17, 2013, 09:30 AM
    ma0641
    Just connect it without the capacitor. Should go through a relay controlled by the thermostat or control board.
  • Jun 17, 2013, 09:55 AM
    maindoug321
    Quote:

    Originally Posted by ma0641 View Post
    Just connect it without the capacitor. Should go through a relay controlled by the thermostat or control board.

    There is no wiring diagram left to view unit is very old. What should I be looking for?
  • Jun 17, 2013, 01:06 PM
    ma0641
    If it is a 1 speed motor without a capacitor, find the incoming supply line and connect hot(usually black) to one terminal and neutral(white) to the other. If it rotates the wrong way, reverse leads. If there is more than 2 terminals you may have a 2 speed motor and will have to determine what wire combination provides the best speed is best for your system.
  • Jun 17, 2013, 07:40 PM
    mygirlsdad77
    Sounds like you have the wrong motor for your condenser. Every condenser fan motor requires a run cap. If you can prove otherwise, I will have learned something today.

  • All times are GMT -7. The time now is 10:08 PM.