How do I check the blower motor on my rheem rqpm-a030jk
![]() |
How do I check the blower motor on my rheem rqpm-a030jk
Check for what? Speed, air flow, trouble starting, smells hot??
Most failure to start or run is due to a bad capacitor. They overheat and fail. Cheap and easy to replace, $20 or so DIY. Typically located on the air handler motor case. Get from an HVAC supply store and make sure to bring the old one with you. Some are round, some rectangular with 2-4 wires. Need to check other things too but I would replace the capacitor first. Could be a bad motor or board. Make sure you are getting voltage to the capacitor but be careful, they generate high voltage. You can set fan to run continuously from the thermostat but still need the capacitor to start and possibly run, depending on model.