Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Electrical & Lighting (https://www.askmehelpdesk.com/forumdisplay.php?f=105)
-   -   Light/dark sensor (https://www.askmehelpdesk.com/showthread.php?t=749694)

  • May 19, 2013, 04:06 PM
    ryan19
    Light/dark sensor
    I have lighting attached to a light sensor and want to add an outlet that will be always hot. I have red, black and white wires (red feeding from the breaker box and tied into the sensor). I capped the red coming in, leaving the red from the sensor connected to the 4 black. 4 white/neutrals tied together.
  • May 20, 2013, 12:37 AM
    JoeDunn
    Ryan19,

    What you said about the breaker box makes no sense.

    Is this a MWBC with a Red wire on one breaker pole and a black from the same cable on another breaker? Or is the "breaker box" with the multi black-white and red conductor, really just a junction box?

    You do realize that adding a new outlet is not considered maintenance. Depending on its location you might be required to install Arc Flash or GFI protection.

    Either way, it requires a permit and inspection. For $15 and the protection of your family... get the permit and have your work inspected!

    Joe
  • May 20, 2013, 01:16 AM
    JoeDunn
    FYI:

    It's actually called a "dusk to dawn" or "photo" sensor