-   -   8-4 romex amp rating @ 130 ft. (https://www.askmehelpdesk.com/showthread.php?t=747987)

  • May 8, 2013, 11:54 AM
    stevestoy
    8-4 romex amp rating @ 130 ft.
    What is the amp rating for a 130 foot run of 8-4 romex?
  • May 8, 2013, 11:59 AM
    ma0641
    Amp rating doesn't change regardless of length. Voltage drop is the issue and it affects motors, compressors etc. What are you planning on this circuit?
  • May 9, 2013, 08:51 AM
    stevestoy
    Installing a 7 ft. square spa with 220v motor and heater. Label on spa connecting box is stating 50A service.
  • May 10, 2013, 06:31 AM
    Dr_Spa
    Romex? Code for wiring pools and spas requires that the supply circuit includes a ground wire that's insulated and of equal size to the other wires. Romex does not meet this requirement.
  • May 10, 2013, 08:47 AM
    stevestoy
    Wow, OK, thanks. I'll check codes and a local supply house for what's needed. Thanks again.