-   -   Square d 50 and 60 amp gfi (https://www.askmehelpdesk.com/showthread.php?t=745719)

  • Apr 23, 2013, 06:45 PM
    JIM CAT
    Square d 50 and 60 amp gfi
    I had a square d qo250gfi with a neutral wire I want to replace it wi th a qo260gfi with no neutral wire on a hot tub that requires two hots and a ground at 230 volts can it be done
  • Apr 24, 2013, 07:18 AM
    hfcarson
    Are you saying that the 2 pole 60 amp breaker "does not" have a white lead?
  • Apr 25, 2013, 04:09 AM
    stanfortyman
    A) Why are you replacing it with a larger breaker?

    B) All GFI breakers do require the line neutral connected. If the breaker does not have a tail then it either requires a jumper wire to the neutral bar (which I have never seen on any GFI breaker), or the tail was cut off and the breaker is useless.