    How to wire a condenser fan motor capacitor
    I went from a 3 wire fan to a 4 wire fan. 1 black, 1 white, 1 brown and 1 brown with white stripe. I wired the 3 wires as before to the capacitor. I attached the brown/white wire to the terminal next to the brown on the capacitor. The fan turns, but slower than before. I removed the brown/white wire from the terminal and the fan speed increased significantly. Should I leave it off and cap it or what?
  • Apr 11, 2013, 04:23 PM
    mygirlsdad77
    There must be another wire hooked to the capacitor coming from the contacter. This wire is powering the capacitor, so you can merely leave the brown/white unhooked and cap it off. Or you can unhook the wire from the contactor and hook the brown/white up there and it will do the same thing. Easiest would be to simply leave the brown/white unhooked and wire nut it. Now, all that being said, if you could post a pic of your wiring, showing capacitor and contactor, we could verify this. This should all be shown in the wiring diagram of the new motor.
  • Apr 12, 2013, 06:25 PM
    Grady White
    Another way to wire it is: Black to one side of the contactor, White to the other, Brown to one terminal of the cap, Brown/White to the other cap terminal.