-   -   100 amp panel for detached shed (https://www.askmehelpdesk.com/showthread.php?t=743146)

  • Apr 7, 2013, 07:04 PM
    Dice god
    100 amp panel for detached shed
    What size wire to hookup a 100 amp panel for a detached shed 26 feet from main house 200 amp panel?
  • Apr 8, 2013, 04:21 AM
    hfcarson
    Fast answer? I assume this is 240V, 1-phase, (3)-#4 THWN cu + (1)-#8 ground...
    Will this be underground? Be aware you need to keep your neutral bar in the panel isolated from the equipment ground and install a ground rod...
  • Apr 8, 2013, 04:31 AM
    stanfortyman
    I don't like answering these simple "What size wire" questions. I am always afraid of all the other unanswered questions. The wire size is only one small part.
  • Apr 8, 2013, 04:35 AM
    hfcarson
    Agreed... I hope for additional contact by the poster.