-   -   2ton condenser with 3ton evaporator without txv (https://www.askmehelpdesk.com/showthread.php?t=741568)

  • Mar 28, 2013, 08:02 PM
    john_doe_2013
    2ton condenser with 3ton evaporator without txv
    I have a 2 ton outside condenser with a 3 ton evaporator coil - goodman units. The TXV installed on the evaporator is malfunctioning. Can I run a 2 ton condenser with a 3 ton evaporator by uninstalling the TXV (no metering device). How well would the system function. Since I use the AC extremely infrequently (few days/month in summer) this shouldn't be a problem - at least that's what I think.
  • Mar 29, 2013, 06:38 AM
    wmproop
    OK,, I hear what you think,, but are you going to expect the unit to work/cool your home?
  • Mar 29, 2013, 06:52 PM
    Grady White
    If you do that, which you are not allowed to do unless licenced by EPA to work with refrigerants, you will destroy your compressor.
  • Mar 30, 2013, 08:10 AM
    mygirlsdad77
    No it won't work at all, and yes you will destroy your compressor right away.