Can I run 6-500kcmil and 2-350kcmil use-2 wire in a 4" grc conduit for line side power to a 600 amp disconnect
![]() |
Can I run 6-500kcmil and 2-350kcmil use-2 wire in a 4" grc conduit for line side power to a 600 amp disconnect
What does your foreman say?
What do the prints say?
This is a big question for someone to come to a home & garden DIY message board to ask. What is your role in this job?
The quick answer is no. And you also may not be able to use 500 parallel for a 600A 3-phase service either.
Do you own a code book? All of this can be found in about 30 seconds in a code book.