I have a house on my farm, 330 feet away is my new woodworking shop. I can power the shop in 2 ways and would like to know which one is the best. With option A, I can have a single meter dual 200 amp service panel base. One line to the house and the other would be to the shop via 4/0 Qualplex service underground. The shop would have a 200 amp service panel in it. With option B, I would have a single 200 amp service panel in the house and run a line to a 100 amp sub panel in the shop via 2/0 Quadplex. Power from an overhead line is too expensive and the 200 amp shop panel and wiring cost twice what the 100 amp sub panel would cost. According to the amp draws from the motor tags, the 100 amp panel is sufficient (including the 80% amp drop due to the line length). I have a single phase air compressor that draws 29.7 amps, the other machinery is 3 phase machines running from a 10 hp Rotary Phase Converter that pulls 26.8 amps on start-up and 13.4 amps at idle. My 5 hp dust collector and table saw draw 13 amps at start-up and 6.5 amps running. I'm a 1 man shop so I would mostly have only 2 machines running at the same time. Which set-up do you guys recommend?