Hot water heating system,boiler not turning off,all 4 jones set to lowest, but all still hot and circulating
![]() |
Hot water heating system,boiler not turning off,all 4 jones set to lowest, but all still hot and circulating
One pump with four zone valves, or four separate pumps?
Thanks, I have found the problem,2 zone valves were stuck open,helped the spring by pushing on the big gear with small screwdriver and putting some moveit(oil) on the valve shaft and moving back and forth.works for now I will change the zone valves in summer time
Thanks for the update.