  • Feb 16, 2013, 03:26 PM
    tidesny
    Goodman GMP 100-3
    The furnace stars (inducer runs) ignitor lights up and then the flame sensor turns on the blowers for about a minute or so. The furnace turns off, blows cold air and then it locks out (1 blink). The furnace does not give me any other blinks but the 1.
  • Feb 16, 2013, 04:59 PM
    hvac1000
    How long does the gas flames stay on?
  • Feb 16, 2013, 05:33 PM
    tidesny
    Quote:

    Originally Posted by hvac1000 View Post
    How long does the gas flames stay on?

    It stays on for about 30 seconds at times and then a few minutes but not longer than 5 minutes
  • Feb 16, 2013, 05:55 PM
    hvac1000
    3 Attachment(s)
    Quote:

    Originally Posted by tidesny View Post
    It stays on for about 30 seconds at times and then a few minutes but not longer than 5 minutes

    It is possible the flame sensor is dirty. Try cleaning it.
  • Feb 16, 2013, 06:08 PM
    tidesny
    I`ve cleaned it several times and it still has the same problem.
  • Feb 16, 2013, 06:49 PM
    hvac1000
    Are the orifices screwed in on your furnace? If so remove the offending burners orifice and make sure it is clean. Remember to use pipe dope on the threads when you screw it back in.
  • Feb 18, 2013, 11:20 AM
    tidesny
    Quote:

    Originally Posted by hvac1000 View Post
    Are the orifices screwed in on your furnace? If so remove the offending burners orifice and make sure it is clean. remember to use pipe dope on the threads when you screw it back in.

    All the burners light up with a blue flame. Yesterday I turned it on and it stood lit for about 10 minutes.
  • Feb 18, 2013, 12:52 PM
    hvac1000
    So it is working?
  • Feb 18, 2013, 05:10 PM
    mygirlsdad77
    Keep us posted if it fails again.
  • Feb 18, 2013, 06:13 PM
    tidesny
    No sad to say.. I just ordered the limit switch...
  • Feb 27, 2013, 05:56 PM
    tidesny
    It turned out to be the circuit board, have heat now finally. Lol
  • Feb 28, 2013, 05:21 PM
    mygirlsdad77
    Thanks for the update.