    Why does the main burner stay lit, only when the gas furnace has warmed up?
    Has to jump from pilot to main valve to give gas valve 24 volts
  • Feb 9, 2013, 07:30 PM
    mygirlsdad77
    Because pilot flame sensing device (most likely a flame sensor) is not sensing the pilot, therefore not allowing power to the main valve. Either that or a bad ignition module. Don't be jumping the gas valve anymore. You need to have this checked by a qualified tech and have it fixed before you endanger yourself any further. Im assuming you have an intemitant spark/pilot ignition module/control? Something along the lines of either a white rodgers, or honeywell s8--- (fill in the blanks for me.)