  • Feb 8, 2013, 11:05 AM
    jrodi
    Electrical requirements
    Have 30 amp circuit breaker (#10 wirer) to cook top. New cook top needs 40 amps.
    Can I add a 20 amp circuit (#12 wirer) to the #10 wires coming into the new cook top to meet the 40 amps required?
  • Feb 8, 2013, 11:26 AM
    stanfortyman
    Absolutely not.
    You need a new 40A circuit run.

    Several code and safety rules prohibit this.
  • Feb 9, 2013, 07:48 AM
    ma0641
    Although your solution sounds good from a wallet standpoint, its also a good way to burn down your house with the new stove too. 4 wire #8 most likely needed.