Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Heating & Air Conditioning (https://www.askmehelpdesk.com/forumdisplay.php?f=150)
-   -   How many baseboard heaters on 30 amp breaker (https://www.askmehelpdesk.com/showthread.php?t=732528)

  • Feb 5, 2013, 09:29 PM
    burntalot
    How many baseboard heaters on 30 amp breaker
    Can I run two 2500watt 240 volts heater s in two separate rooms with two thermostats on the some 30 amp breaker
  • Feb 6, 2013, 09:02 PM
    Grady White
    Yes, as long as you have #10 copper wire. The two heaters combined would draw aprox. 21 amps. Do not try to use any lighter (higher gauge) wire.
  • Feb 6, 2013, 11:42 PM
    scott53715
    This all depends on how many watts your heater draws. They should be labeled. Now you need to convert Watts to Amps. Watts divided by Volts equals Amps. (wish I new how to find simple math symbols on this complex computer). As an example 12 Watts/ 12 Volts = 1 Amp. Therefore if you have 120 volts at 30 amps you max is 3,600 watts. If everything is done correctly (proper wire size et. al.) I wouldn't go over 80% of that to be safe.