    How brittle are Copper Clad Aluminium conductors?
    I worked on a main service panel today that had two failures.

    1) All of the receptacles on one wall in the living room were dead.
    The failure: The black conductor mounted to CB 11 broke off where the cable
    Went under the breaker screw.

    2) The washing machine receptacle receptacle only showed 37 volts.
    The failure: The Neutral conductor for CB #13 broke off at the screw on the
    Neutral bus bar.

    I thought it was odd and merited a question
  • Jan 22, 2013, 03:32 AM
    tkrussell
    The conductors broke I will bet anything due to a nick in the metal when stripped and then stressed by the tightening of the screws, and possibly heating and cooling effect.