  • Jan 15, 2013, 07:20 PM
    clpcfd
    Urd amps
    Where do if find allowed amps for urd in code
  • Jan 15, 2013, 07:55 PM
    stanfortyman
    Typically it would be in the old 310.15(B)(6), since URD is typically used for residential service entrance.
  • Jan 16, 2013, 03:31 AM
    tkrussell
    However, "URD" will not be found in the NEC, as it is a name for an assembly. Usually URD cable is aluminum wire that uses XLPE or XHHW insulation.
  • Jan 16, 2013, 06:22 AM
    stanfortyman
    Good point. I always forget to mention that.
    Although in the resi service sizing chart they don't mention insulation, just size, right?
    Now I have to go look it up. :/
  • Jan 16, 2013, 06:52 AM
    tkrussell
    Yes, Table 310.15(B)(6), does refer to applicable insulation types .
  • Jan 16, 2013, 09:54 AM
    stanfortyman
    Ah yes! In the title. Funny the things you overlook when you look st something so many times.


    Quote:

    Table 310.15(B)(7) Conductor Types and Sizes for
    120/240-Volt, 3-Wire, Single-Phase Dwelling Services and
    Feeders. Conductor Types RHH, RHW, RHW-2, THHN,
    THHW, THW, THW-2, THWN, THWN-2, XHHW,
    XHHW-2, SE, USE, USE-2
  • Jan 16, 2013, 01:22 PM
    tkrussell
    Doncha just hate it when they hide stuff right in front of us? I do that all the time.