Maximum number of conductors in receptacle box
Hello. If you have two 14/2 with ground cables coming into a 3"x2"x2-1/2" electrical box with a duplex receptacle and internal clamps, is this acceptable by NEC code? All the outlets in my house are wired this way.
Here is my calculation for required electrical box volume:
8 (4 conductors)
2 (ground)
4 (receptacle)
2 (internal clamps)
-------------------
16 cu in.
The 3" electrical box with a duplex receptacle and internal clamps, is this acceptable by NEC code? All the outlets in my house are wired this way.
Here is my calculation for required electrical box volume:
8 (4 conductors)
2 (ground)
4 (receptacle)
2 (internal clamps)
-------------------
16 cu in.
The 3"x2-1/2" box would seem to have inadequate volume. Am I misinterpreting the NEC code? Can someone help me to understand? Thanks.