  • Jan 7, 2013, 10:13 PM
    mbro12
    Subpanel protection
    If I run a 10-3 with ground direct burial to a panel in a small garage and use it to split into to 30 amp curcuits what breaker do I need in my main electrical panel feeding the garage panel?
  • Jan 8, 2013, 04:53 AM
    stanfortyman
    The breaker in the main protects the wire, so seeing as it is #10 you can use a 30A breaker.

    What are you using 30A breakers for in the garage?
  • Jan 8, 2013, 05:44 AM
    tkrussell
    If this is for one 240 volt 30 amp circuit, why the need for a subpanel?
  • Jan 10, 2013, 04:13 PM
    mbro12
    Quote:

    Originally Posted by stanfortyman View Post
    The breaker in the main protects the wire, so seeing as it is #10 you can use a 30A breaker.

    What are you using 30A breakers for in the garage?

    I'm feeding through to a panel in a chicken coup for lights an automatic door opener and outlets for heat lamps
  • Jan 10, 2013, 04:19 PM
    stanfortyman
    Just know you cannot use 30A circuits and breakers for general 15 or 20 amp receptacles and lighting circuits.