  • Dec 13, 2012, 01:22 PM
    freddy3656
    Hvac
    Why my blower doesn't stop
  • Dec 13, 2012, 01:40 PM
    smoothy
    Check your thermostat settings... most have a switch for the blower to run constantly or to be automatic...
  • Dec 13, 2012, 06:38 PM
    Grady White
    If the fan is controlled by an old style fan/limit switch it may be sticking.
  • Mar 11, 2013, 08:52 AM
    nvdragon1
    If it does it in cycles check your filters for the limit switch (if thers no button it will auto reset and be a headache ) on most newer units the fan running and not firing is a fault indicator i.e.. . limit switch (push buttons between the LOW voltage wires ) pressure switch ( vent system ).. if you have a blinking light on the circuit board count the flashes and it will let you know which one it is.. Ive been hvac tech for 23 years.. number 1 cause or faults is dirty filters and will cause A lot of other problems..