Rheem criterion gas furnace control board
Control board I replaced was from a Rheem criterion gas furn model number is RGDG 10eamer or CW 5D302 - F0294 7885
The board replaced was Honeywell MPLS MN 55422 24v 60hz
Called wholesaler said that number didn't make sense long story short that board number no longer used phased out , heard him talking to self said maybe one of 2 boards lol I purchased ICM288 replacement board
Have same prob now every one has with Rheem flame kicks on 5 sec or so kick offf does that twice sits for like 5 min blower running of course then goes through cycle again flame light never comes on I clean flame sensor all limits , and safety's have correct volt and or continuity , I tested the flame sensor red lead on red black on seņors my micro amp reading bounced from -1 to 3 says in trouble shoting if below 1.0 then needs replaced thing is when flame came on it wouldn't stay on anything kept bounce like no flame even came on, would you say it is bad before I lite up dealers phone ? Or any other suggestions before I use TNT to fix this thing, also the 80%er's are no more as of may 1st 2013 so get them while there hot can't install them legally and dealer are trying to get rid of stock goingt o 90% only