  • Nov 19, 2012, 12:13 PM
    pastor1189
    Dryer Wiring
    Been without a dryer for a number of years. Found the 30 amp breaker.
    But cannot find the wiring yet. Wall where the dryer use to be has been boarded over. Circuit box is only about 12 feet away from dryer bay.May have to rewire from the breaker box (Not Me) to three prong flush receptacle which is also missing. Do not want to order the dryer yet. Until the line is finish. Some have suggested 8 gauge wire. Is that good for a 12 foot run? Use to a dryer there about 10 years ago.
  • Nov 19, 2012, 01:52 PM
    donf
    If you are going to rewire, you might as well have the work done properly.

    First, read the electrical instructions for the dryer. Normally a 40 amp double pole breaker is required along with a 4 wire 8 AWG cble and a four wire receptacle.

    You really do not want a three wire system.
  • Nov 19, 2012, 02:12 PM
    pastor1189
    The other dryer in the past was a three prong and a three prong receptacle
    On a 30 amp breaker .Okay thanks for the advice
  • Nov 19, 2012, 02:39 PM
    ma0641
    That is old code, new is 4 wire, 2 hots, a neutral and a ground.
  • Nov 19, 2012, 02:56 PM
    pastor1189
    Sounds inviting . Since I am starting from scratch why not go with 4 wires.setup.
    The dryer can take 3 or 4 wires. Even if the house was build in 1951
  • Nov 19, 2012, 04:00 PM
    pastor1189
    I found 40 amp double pole breaker $9.47 A four wire 50 Amp power outlet receptacle $8.99
    I couldn't find 40amp?
    The wire 8 AWG gauge is very thick I wonder how you can wrap a thick wire like that, or maybe it has some kind of fitting that goes into the power outlet?
  • Nov 19, 2012, 04:02 PM
    ma0641
    Quote:

    Originally Posted by pastor1189 View Post
    I found 40 amp double pole breaker $9.47 A four wire 50 Amp power outlet receptacle $8.99
    I couldn't find 40amp?
    The wire 8 AWG gauge is very thick I wonder how you can wrap a thick wire like that, or maybe it has some kind of fitting that goes into the power outlet?

    They don't wrap, they insert under a screw plate.
  • Nov 19, 2012, 04:12 PM
    pastor1189
    Oh boy I am learning. I know the 240 is split between the. Black and Red, Neutral, Ground on the back of the dryer. That makes the 4 wire makeup. I guess you would need a strain relief connector to keep the cord secure.

    I do not know how the breaker itself is wired coming from the dryer with the four wires
  • Nov 19, 2012, 09:42 PM
    ma0641
    In a 240 breaker, if there are 4 wires, red goes to 1 pole of the breaker, black to the other, neutral to the neutral bar and ground to the ground bar. In older homes, the neutral and ground are on the same bar. On a 3 wire - red, black, ground, wired as above .
  • Nov 20, 2012, 05:23 AM
    pastor1189
    Very good. I got it. Thank you