Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Electrical & Lighting (https://www.askmehelpdesk.com/forumdisplay.php?f=105)
-   -   100 amp subpanel for a garage wiring. (https://www.askmehelpdesk.com/showthread.php?t=716043)

  • Nov 11, 2012, 11:02 PM
    temoore86
    100 amp subpanel for a garage wiring.
    I'm wiring a 100amp subpanel for a detached garage. I want to place a 100amp breaker in the house breaker panel to feed the garage. Will #2 aluminum direct burial cable w/ 2 conductors and the shield as the neutral work? If not can I run that cable with a separate neutral or ground wire to the subpanel?
  • Nov 12, 2012, 03:43 AM
    tkrussell
    A "subpanel" needs 4 wire feeder, two hots, a neutral, and an equipment ground conductor. If you want to direct bury cable use #2- w ire URD cable.