upgrading to 200 amp with connection issues
Aloha Friends,
I am renovating our newly purchased home. We have a meter main with the shutoff in our detached garage that runs underground with 2-0 aluminum to feed our 100 amp panel. We are bringing in the following electrical load:
•[20 x 5 = 100 amps] five A/C's all 110 volt (five AFCI protected 20 amp circuits)
•[50 amps] 220 volt stove circuit
•[20 amps] 110 volt refrigerator circuit
•[20 amps] 110 volt dishwasher circuit
•[20 amps] 110 volt disposal circuit
•[30 amps] 220 volt dryer circuit
•[20 amps] 110 volt washer circuit
•[15 x 2 = 30 amps] whirlpool tub (two 110 volt GFCI protected circuits)
•[60 x 2 = 120 amps] two 220 volt tank less water heaters drawing 60 amps each (three showers, three sinks, dishwasher, whirlpool tub and washer machine)
•[20 x 2 = 40 amps] two 110 volts GFCI protected 20 amp circuits for each of the two bathrooms
• [20 x 3 = 60 amps] Three 110 volt GFCI protected circuits for the kitchen counter and Island
•[20 amps] one 110 volt AFCI protected circuit for three bedrooms
•[20 amps] 110 volt circuit for the office
•[20 amps] 110 volt living/dining room circuit
•[20 amps] 110 volt lighting circuit
•[15 amps] 110 volt burglar/smoke alarm system
•[20 amps] 220 volt outdoor circuit
•[20 amps] 110 volt outdoor circuit
•[20 amps] 110 volts garage/sidewalk lights circuit
In addition, I want to add a 60 amp breaker and install a subpanel back in my garage. I need one 220 volt 30 amp outlet for a future welder. Two 110 volt 20 amp circuits for saws and power tools and one dedicated 110 volt 15 amp circuit for my air compressor.
All together, that’s OVER 700 AMPS! :eek: Now I know that not every circuit will be running all at one time, nor will each circuit be drawing full power, most likely only during startup will the appliances pull their rated load.
We're upgrading from 100 to 200 amp indoor panel and changing our meter main w/shutoff to 200 amps instead of 100. I want to save as much as possible as copper is very expensive. So I believe that calls for 4-0, 4-0, 4-0, 2-0 SER Aluminum to cover the 80 foot span from the meter main to my indoor panel. I’ll have to abandon the underground conduit as it is only 1 ¼” and holds three 2-0 aluminum wires (2 hots and one neutral) and one ground for the old panel.
My first option, should I keep the existing wires and just upgrade to 150 amps as that is the max that 2-0 aluminun can go with? To me, that’s just too little. Running two showers will crank both tank less heaters which draw near the 60 amp load each initially, meaning that I’ll be chomping up 120amps just running two showers. In a family of five, that will most likely occur daily in the morning and in the evenings. With 30 amps left, my stove will trip the main if we cook while the kids shower. Just not appealing so I think this is a waste of an idea…but I’m willing to listen if anyone can convince me that leaving everything and just upgrading to 150 from 100 amps is the way to go. That’ll be the most quick, easiest way though.
My choice is to upgrade to 200 amps and give us some room to spare. To keep it affordable, I’m looking at getting 80 feet of 4-0, 4-0, 4-0, 2-0 SER Aluminum cable. I’d have to come out the top of the main breaker shutoff, run the SER just under my garage joists, through the closet wall, out the other side and straight across the yard running along the hollow tile wall staying up at about eight feet high, making a slow 90 bend up the eave and into the attic space, making another slow 90 bend and run straight to my utility closet and one more slow 90 bend down and straight into the top of my indoor panel. This seems to be pretty straight forward but here’s some of my concerns.
1. The old 100 amp panel had four wires and the neutral and ground bars were not bonded. Two hots, one neutral and one ground. All running back to the main shutoff where the neutral and ground are bonded. But the odd thing is that the panel also included a ground that ran from the indoor panel ground bar to the nearest water line and grounded on the copper water line. If I’m not mistaken, is this not an incorrect application of the ground, or do I need to make sure that I include this second ground on the new panel?
2. Since the new panel is 200 amps, will the 4-0 SER cable be able to enter the panel through the top and fit in the hot and neutral main lugs? Although the lugs are pretty big, the 4-0 aluminum looks to be very large, will they fit in the main lugs on the indoor panel? What size do I need to punch out the top of the indoor panel so the SER fits nicely?
3. The new meter main with shutoff is also concerning me with connection issues. Won’t the 4-0 SER have to be connected to the double pole 200 amp breaker? Those connections are even smaller then the main lugs on the indoor panel, how will they fit the SER cable in those small connections? Will I need to use a large JB to hold my splices and step down to 2-0 copper lines just above the main shutoff and will the 2-0 fit into the breaker? If I do, will I need to use 3” conduit to enclose the copper wires? Will I need to do that at both the meter main and the indoor panel? I have seen a Siemens type 200 amp main breaker that looks like a light switch, is very large at about two inches wide by six inches long. That breaker had two huge lugs on both ends, very different than the normal single and double pole breakers normally used. That looked like it would easily fit.
4. Would it be best to get a main shutoff that had some extra breakers so I could just run my garage circuits straight from the main instead of running circuits back out from the indoor panel to a subpanel?
5. If I need to step down in wire size to 2-0 copper, can I run them in the utility wall or do they need to be enclosed in 3” conduit right from the JB?
6. is there such a thing as 2-0 copper SER cable with all four wires similar to the aluminum SER cable or are the copper all separate?
7. Is my only other option to run three 2-0 copper wires from my shutoff to my indoor panel? What is the minimum size of the ground wire if I’m running 2-0 hots and 2-0 neutral?
8. If I'm to splice from the 4-0 alu to 2-0 cu, what do I use for that splice? :confused:
Please help!
thanks again friends,
alohabob