How to run 120 volt incandescent from 277 volt circuit?
*Threads Merged*
![]() |
How to run 120 volt incandescent from 277 volt circuit?
*Threads Merged*
You can't.
Let me rephrase my question. The house panel is 277/480 and the lighting circuit is 277 v. I want to add some 120 chandeliers. I'm hearing that you can purchase 120/277 magnetic transformers for this situation but they only go to 300 VA, is this possible?
Here's a 5KVA , 277V primary/120V secondary general purpose transformer
http://www.acmepowerdist.com/datashe...-2-79744-S.pdf
Selected from this page (group VII)
Acme Electric
Have an electrician install it for you.
I'm asking about a lighting transformer. The type that you install on a 4 square j box. I can only find 300 volt amp for $60
You said "chandeliers" without specifying the load and asked for more. Chandeliers can be huge...
http://www.lightinguniverse.com/chan...ductItemsImage
This is obviously a commercial setting so your only option is to call an electrician.Quote:
The house panel is 277/480 and the lighting circuit is 277 v.
Any place that has a 277/480V service must also have an on site transformer with 120/240v or 120/208v panels. This is to get you standard 120v receptacles.
HaHaHa... Not likely.Quote:
Can I get lighting transformers for less than $60 or higher than 300 VA?
Call an electrician and see what your options are.
What brand panels and type of breakers? I'm guessing bolt on breakers, tell me the letter designation
For example Siemens BL or Square D BOQ or CutlerHammer BL, It will be a paper tag on each breaker you have to remove the deadfront to read the teeny tiny print.
Adding small transformers for lighting, unless it is only one fixture, is a bandaid approach. How many 120 volt fixtures are you planning to add?
| All times are GMT -7. The time now is 03:54 PM. |