Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Heating & Air Conditioning (https://www.askmehelpdesk.com/forumdisplay.php?f=150)
-   -   When heat is on the outside fan comes on for 5 seconds shuts off and comes on again (https://www.askmehelpdesk.com/showthread.php?t=710923)

  • Oct 22, 2012, 09:47 AM
    ted123
    When heat is on the outside fan comes on for 5 seconds shuts off and comes on again
    Bryant unit>>>when heat is on the outside fan comes on for 5 seconds shuts off and comes on again for 5 seconds and shuts off is this normal? The fan inside the house is running but there is no heat. After 90 minutes of the fan running I turned up the heat by 10 degrees. The red light came on and the temp inside started to go up. So if I just leave the temp at a certain degree the red light comes on for a short period but goes off and the house never gets warm unless I raise (way up) the temperature inside??
  • Oct 22, 2012, 07:20 PM
    Grady White
    Presuming this to be a heat pump, the red light indicates the electric strip heat is on. The problem with your outdoor unit could be a low refrigerant charge, bad pressure switch, or bad contactor.

  • All times are GMT -7. The time now is 11:24 PM.