  • Oct 3, 2012, 11:55 PM
    zijad
    Sub panel
    I want to set subpanel for cople lights end outlets 1electric range end 1drayer .what size wire I nead to use from Maine panel
  • Oct 4, 2012, 02:52 AM
    tkrussell
    4 wire #2 aluminum SER cable will work fine.

    Are you sure the Main panel can handle the added load?
  • Oct 4, 2012, 09:04 AM
    zijad
    Sub panel
    You mean 1wireb4/2 or more wires
  • Oct 4, 2012, 10:09 AM
    tkrussell
    Do not start a new thread, just reply to the same question you started.

    I merged your two tehreads.

    I mean a 4 conductor cable, has 4 # 2 wires, in a cable called SER.

    Where are you located?
  • Oct 4, 2012, 12:29 PM
    zijad
    Quote:

    Originally Posted by zijad View Post
    You mean 1wireb4/2 or more wires

    I mean to run 4/3 wirr with 60 amp breker in mi subpanel.then from subpane run8/3 for ranhge with 40 amp.end 10/3 wire foer drayer with 30amp breker