How can I get the LED codes for the Carrier 58ZAV? I don't have the manual. The unit won't run and is flashing a 2-4 code.
![]() |
How can I get the LED codes for the Carrier 58ZAV? I don't have the manual. The unit won't run and is flashing a 2-4 code.
Quote:
Originally Posted by unclebobtx
Code 24 might be a open fuse (open secondary), look to the purple 3 amp fuse on the control board, just pull it off and look at the element. Something in the circuit may be causing the fuse to blow and should be looked at . Take caution and do not exceed 3 amps on the replacement fuse,
That's all I got without actually being there
Thanks for the help. The fuse was out. I replaced it and the fan came on. However, the fuse went out again as soon as the thermstat called for the compressor to come on.Quote:
Originally Posted by juggallojed
Any other suggestions??
Either the contactor or the control wires are grounded