Concord Gas Furnace with run time problems.
We have a Concord Gas Furnace that is about 3 years old. The furnace seems not to respond to the thermostat. We replaced the thermostat with a new digital one but are still experiencing the same issues.
We set the thermostat to 83 just as a test. I had my wife record when the furnace came on and when it went off along with the temp. at both times.
The furnace comes on around 70 and runs for about 30 minutes and then turns off. The temp is 71 or 72. The temp. in the house never reached 83.
The furnace has a honeywell control board ST9160A1002 on it. The thermostat is a 4 wire (G,Y,W,RH) RC & RH are jumpered together in the thermostat. The control board has G,Y,W,R,C on it. The RH wire is hooked to R.
I watched it run once and it came on at 71, the temp on the thermostat dropped 2 degrees to 69. The furnace ran for 35 minutes and turned off at 71 again. The thermostat was set at 83 degrees.
Any help would be greatly appreciated?