Is my 100 amp panel overloaded?
My main panel is 100 amps and was completely full with about 10 breakers. About 5 years ago I had an addition put on the house and the contractor said that the service would need to be upgraded (but didn't specify how). After the licensed electrician left ,I realized that he had installed a subpanel in the garage with 4ga copper wire with 8 more breakers on it and a 60 amp breaker for it in the main panel . This was all inspected by the town and approved.
I had no problems till about a month ago when the lights (only those coming from the subpanel) started dimming. ALOT(I measured a voltage drop of >15v for a few seconds). I had the local power company come . They replaced all connections to the house and wires on the poles and the neutral block in the meter pan. No signs of water in the meter pan. The main panel had signs of moisture/rust from when the house was first built 24 yrs ago and the basement was damp. The main breaker had residue of rust leaking from the switch. I replaced the main 100 amp breaker. One contact was rusted ,the other looked burned. I had to clean up the buss bars before installing the new main. The problem stopped for a short time but is back.
I haven't pulled the main breaker to inspect it but I'm wondering if my service should have been upgraded to 200amps before adding the subpanel?
Any thoughts on this would be appreciated. Thank you.