  • Sep 10, 2012, 03:01 PM
    Jherrera323
    Standard size for fuses and inverse circuit breakers
    Which of the following is not a standard size for fuses or inverse time circuit breakers? 45A, 70A, 75A, 80A, And where can I find it on the nec
  • Sep 10, 2012, 03:21 PM
    stanfortyman
    Which of the following is a homework/test question?


    A-
    Quote:

    Originally Posted by Jherrera323 View Post
    Which of the following is not a standard size for fuses or inverse time circuit breakers? 45A, 70A, 75A, 80A, And where can I find it on the nec



    Answer: A





    If this is what you are working on in class I am sure it was gone over at some point. Check your study material.
  • Sep 17, 2012, 07:48 PM
    shuntripper
    240.6(A)

    75A nonstandard

    If you're cheating I'll help you stay stupid, learn where stuff is in the NEC